Alpha cb 50 boiler losing pressure

  • Thread starter Thread starter GC
  • Start date Start date

GC

Joined
2 Aug 2004
Messages
8
Reaction score
0
Country
United Kingdom
Just had British Gas replace the Diverter valve / motor and engineer left only 1 hour ago. Boiler now rapidly losing pressure with hot water exiting through the external overflow pipe. Phoned BG but cannot return til Thursday !

Any advice on likely cause / solutions would be welcomed.

Thanks

GC
 
I wonder if he used the prv to drain the boiler down :roll:

If he did, it has probably got some carp on the seat and sticking open.

Needs a new one in a perfect world if this is the case.

You could try opening and shutting the prv several times quickly to see if this will shift it.
 
Thanks Dave
Opened and shut PRV a couple of times and the fast flow from the overflow has reduced to a drip - still not ideal but at least I can manage til engineers return on Thursday
 
Engineer returned Thursday and volunteered he had used prv to drain down boiler and that there was probably some muck preventing closure !

prv removed and cleaned and everything now working fine

Thanks for the advice
 