Rental EICR just been sent to me for a laugh.
... kitchen sockets and boiler fused switch share common earth, not permitted... 543-01-02
Kichen sockets circuit listed as 4mm² singles 20A MCB.
Boiler circuit described as 1.5mm² singles 6A MCB.
The size of the Earth wire is not listed.
Reading my 2008 regs, 543-01-02 describes the size of the shared conductor. The fact it's been sent to me I assume it hasn't changed [much?]
The only other fault is RCD; 150mA 42/46mS
There is a quote for repair which I haven't seen.
... kitchen sockets and boiler fused switch share common earth, not permitted... 543-01-02
Kichen sockets circuit listed as 4mm² singles 20A MCB.
Boiler circuit described as 1.5mm² singles 6A MCB.
The size of the Earth wire is not listed.
Reading my 2008 regs, 543-01-02 describes the size of the shared conductor. The fact it's been sent to me I assume it hasn't changed [much?]
The only other fault is RCD; 150mA 42/46mS
There is a quote for repair which I haven't seen.