Currently old vented system , S plan , no pump overrun. pump in airing cupboard.
Moving to system or heat only boiler with separate pressure vessel and existing pump
question is: would I need a live feed from pump only if using heat only boiler?
with system boiler having pump built in I presume live feed not needed?
 
Sponsored Links
A system boiler will almost always need a 4 core supply - permanent live, neutral, earth, and switched live.

Heat-only boilers tend to vary. Some need a permanent Live, some don't. Some need the pump to be wired back to them to provide an overrun, some don't
 
Thanks Muggles
At the moment if the timer turns HW or Heating off the pump also cuts off immediately.
 