Hi Gas Boiler experts, please let me have your thoughts on this fault. With boiler C.H control knob set to "0" the boiler fires up as soon as it is powered up. The radiators heat up very slowly, (I cannot hear the gas valve switching the solenoid for high gas flow rate) Gas flame height looks lower (than what I normally see)
The water pump is running and radiators eventually get extremely hot and the red L.E.D lock out lights up and boiler shuts down. During this heating up phase none of the green led light strip (which indicates water temperature) light up. After 5 minutes or so, the boiler can be fired up again by hitting the reset button, with lockout fault re-occurring consistently a few minutes after.
When the hot water tap is run it's hot for about 10 seconds and then consistently luke warm (regardless of control knob setting.) Again flame height looks fixed and on low set point.
With so many things apparently not operating I was thinking to change the P.C.B. ? But before I do that, could it be the temperature sensor reporting an inaccurate low temperature and the boiler automatically firing up in a frost protection mode? This could explain it also eventually allowing the boiler to over-heat. But would the led sensor not light as the temperature increased? I guess these are also linked to the sensor response so probably not. Any body seen this issue before? Thanks.
The water pump is running and radiators eventually get extremely hot and the red L.E.D lock out lights up and boiler shuts down. During this heating up phase none of the green led light strip (which indicates water temperature) light up. After 5 minutes or so, the boiler can be fired up again by hitting the reset button, with lockout fault re-occurring consistently a few minutes after.
When the hot water tap is run it's hot for about 10 seconds and then consistently luke warm (regardless of control knob setting.) Again flame height looks fixed and on low set point.
With so many things apparently not operating I was thinking to change the P.C.B. ? But before I do that, could it be the temperature sensor reporting an inaccurate low temperature and the boiler automatically firing up in a frost protection mode? This could explain it also eventually allowing the boiler to over-heat. But would the led sensor not light as the temperature increased? I guess these are also linked to the sensor response so probably not. Any body seen this issue before? Thanks.