I am in the process of having a hefty pair of drive gates automated. The cable run from the house is 100 feet. I am told that 1.5 twin and earth will suffice. Can anyone advise please? I don't think the motors have a very high load. Thanks
I've done a few lekky gates. 1.5mm is fine for that distance but SWA, not t&E. Also 1.5 SWA from one gate to the control box. You'll need 3core for that as you have fwd revers and common for the motor.
Put all SWA in a service duct so u can pull in more wires that you forgot.
Connx for control suff (magic beam etc) I run in CAT5 down the svc duct.
Never had any probs except when clients meddle with the settings.![]()
Will u have a buried inductiive loop as a gate opener? I use T&E for that and connect up the three cores in series so you get a three wire loop if you get my drift.
This is OK for domestic driveway. Read raoadways need much tougher cable for the loop.
Thats great. Thanks. I wont bother with the inductive loop gate opener as I could have bought a new car for what these gates are gonna end up costing! Or is that false economy?