Back 80HE stuck pressure differential assembly?

Discussion in 'Plumbing and Central Heating' started by Jon2412, 12 Mar 2017.

  1. Jon2412

    Jon2412

    Joined:
    12 Mar 2017
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    hi all,

    I have a Baxi 80He boiler. Rads we're working fine but no Hot water.

    Have checked that the flow sensors were working, pump was clearly working, system pressure correct, boiler firing as expected and temp sensors indicating rise in water temp on the front display.

    I noticed in hot water mode that the boiler feed and return pipes were baking hot. The motorised actuator on the diverted valve is operating and the water flows through the how water pipes around the boiler. (I checked by touching and checking the in/out flow pipes going to the expansion vessel at the back of the boiler) However the heat exchange plates remained cold whilst bypass pipe got very hot. Rads are not heating up when hot water is demanded so this all indicates to me that the main diverter valve is operating as expected.

    I have taken off the plate heat exchange and it's not clogged. I have removed the front diaphragm on the pressure differential value unit and it is working and freely moving however I have now seen that the pin in the main body of the differential valve assembly appears to be stuck in?

    Having done all the other checks this would appear to confirm that water was only being diverted into bypass and back round the boiler.

    Is the assembly something that can be refurbished or should I be buying a new unit? It's a real pain to get out as I can't quite get in to undo the bypass pipe feed, so before I take it any further and buy a fairly expensive unit I wanted to check if anyone had other thoughts!

    Thanks for any advice/thoughts!
     
  2. Sponsored Links
  3. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    I normally replace the whole assembly for a customer.

    But it is possible to take it apart and clean it and reassemble.

    Once I did that for a customer friend and spent a while even boiling the bits in citric acid. But it still jammed again a few weeks later. So never again.
     
    • Thanks Thanks x 1
  4. Jon2412

    Jon2412

    Joined:
    12 Mar 2017
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks Agile. Does sound like it might be false economy to try and clean it up. I don't relish the idea of going through all this again in some weeks time! Between my time and replacement gaskets and things I think I shall pay up for a new assembly.

    Though how on earth am I supposed to get the nut undone for the bypass pipe feed?! I've got the HW HeatEx and Pump out and I'm still struggling to get onto the nut and get some leverage (without bending the bypass pipe). It's not the easiest of access points!

    Thanks
     
  5. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    Those are the joys of repairing boilers!
     
    • Like Like x 1
  6. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,800
    Thanks Received:
    2,567
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Those are the joys of repairing combi boilers!

    Heat only boilers are so much less hassle for a RGI to repair.
     
    • Like Like x 1
  7. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    Bernard has never repaired any boilers of course.

    Particularly not the Ideal Isar heat only boiler,
     
  8. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,800
    Thanks Received:
    2,567
    Location:
    Bedfordshire
    Country:
    United Kingdom
    I think I have in the distant past. but never a combi.....
     
  9. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    Or even noticed my intentional mistake.
     
  10. Sponsored Links
  11. FlyingFish

    FlyingFish

    Joined:
    8 Jan 2017
    Messages:
    83
    Thanks Received:
    12
    Country:
    United Kingdom
    Sounds like your talking about the INSTANT version of that boiler, and its the pin in the preheat diverter thats stuck (common fault).

    You need a sturdy tap spanner (see link below for the one I use) with a wrench on the end to get the back nut undone, but in all honesty if the pin is showing no signs of leakage then you might as well remove just the front nut, clean/polish the pin and regrease. Take care not to distort that front nut when you undo it, as the P'Diff has got to fit back into it.

    https://www.cromwell.co.uk/shop/han...nch-adjustable-basin-nut-wrench/p/MON5880345V
     
  12. Jon2412

    Jon2412

    Joined:
    12 Mar 2017
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    Flyingfish - thanks. It is indeed an instant version, my bad for not noting this up front.

    Thanks for the advice on the tools - looks like I might need to buy one!

    The front part of the assembly doesn't look like it is a screw fitting? The p/diff just sits on it with a clip and I see no obvious threaded section that would unscrew. Certainly it would make life easier if it did. Am I missing something, it looks like it's a solid unit (and no there's no sign of water leak so guessing gunked up internally)

    Thanks
     
  13. FlyingFish

    FlyingFish

    Joined:
    8 Jan 2017
    Messages:
    83
    Thanks Received:
    12
    Country:
    United Kingdom
    It does unscrew, and if it's dry, then go for it. It will be fairly tight, you just need to grip it without squeezing it. The force required can distort the round shape of your not careful. Depending on the tool you use. Normally a stubby wrench can do the job. Pliers can crush tho.
     
  14. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    14,790
    Thanks Received:
    3,251
    Location:
    Glasgow
    Country:
    United Kingdom
    The castellated nut that takes the clip will screw off
    You will get wet if pressure is not zero
    Almost certain that part will be seized
    Last one I cleaned and lubed. Unless leaking, have never had to replace the whole manifold
    We like to call ourselves engineers , but then revert to part changing, not very engineering in my book
     
    • Like Like x 1
  15. Jon2412

    Jon2412

    Joined:
    12 Mar 2017
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    Ah okay thanks for this, that will make life a little easier perhaps. System is drained so no pressure in it and the inside of the nut is bone dry with no sign of leakage. Thanks for your replies. Most insightful.
     
  16. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    Which are you trying to remove?

    The one on the left with the motor actuator?

    Or the one to the right with the diaphragm assembly?

    Or both?
     
  17. FlyingFish

    FlyingFish

    Joined:
    8 Jan 2017
    Messages:
    83
    Thanks Received:
    12
    Country:
    United Kingdom
    It's the preheat valve, mentioned above.
     
Loading...