can a ch system be balanced if the radiators had the trvs and lockshield valves on the wrong pipes? the trv and lsvs are bidirectional (flow both ways)? thanks
As long as the TRVs are bidirectional (usually shown by two arrows at right angles on the body), it does not matter which end the TRV goes on a radiator. Balancing just means adjusting the flow though the rad; and as the water going is just passing through the rad, it does not matter which end the LS valve goes.can a ch system be balanced if the radiators had the trvs and lockshield valves on the wrong pipes? the trv and lsvs are bidirectional (flow both ways)? thanks
There is no mention of the lights in the Britony 100 Manual, though they are shown in all the drawings! My guess is that they are supposed to show what the boiler is doing.what are the row of lights on the front of the boiler ?not the power on burner on, flame lockout lights, the row on the left to it? when the lights drop to 1 or 2 leds the burner light comes on and gas meter spins then the row of light go up to the top (all lit) then burner light stops and gas meter stop. this is happening all the time non stop cycle when in ch mode is this normal?
You need to set the room temperature to a higher setting than normal, say 25C or more, so the boiler keeps running all the time at full output and the water temperature remains constant.2 when measuring the temperature on radiators whilst balancing the rads the temperature goes up then back down then back up etc. i imagine when the burner is running its flowing hotter water. is this normal?
3 if answer to 2 is normal how does one record the temperature as its varying?or when does one record it
They won't cause any problems - the boiler is not the modulating type.boiler c&m britony combi 100, timer danfos old school 103 and room stat honeywell.
You need to let the system heat up from cold so you can determine the order in which they heat up. If you adjust the rads in a random order, you will have problems as adjusting one at the beginning of the chain after one further down the chain will affect the one adjusted first. If you adjust them in order you will minimise this.When balancing i did not let the system cool down nor did i check which order they are served in.
That's good.i did have the boiler temp on full and all trvs on full and all lsv fully open and room stat on full.
There's no point trying to balance an incomplete system!there are 3 more rads i need to put back on the system