Balancing Microbore Question

Discussion in 'Plumbing and Central Heating' started by mustbeunique, 20 Nov 2015.

  1. mustbeunique

    mustbeunique

    Joined:
    20 Nov 2015
    Messages:
    2
    Thanks Received:
    1
    Country:
    United Kingdom
    My system is Gloworm fuelsaver, open vented, twin pipe microbore. I can see part of the pipework - 22mm flow and return feeding 8 mm microbore to 9 rads with TRVs. There is a tenth rad in bathroom directly above the boiler fed by 15mm with wheel valve and lockshield.
    I have assumed this rad has no TRV because it provides a flow if all TRVs are shut. Should I balance this rad using the LS valve or leave it fully open?
     
    • Thanks Thanks x 1
  2. Sponsored Links
  3. ScottishGasMan

    ScottishGasMan

    Joined:
    22 Jan 2007
    Messages:
    6,982
    Thanks Received:
    2,703
    Country:
    United Kingdom
    It should still be balanced with the rest of the radiators if your doing them, especially if it's the only one in 15mm as that will be the easiest route for water to take and will "steal" the flow from the microbore if it's not done
     
    • Thanks Thanks x 1