You have established that the rad that didn't heat up ,will do if it gets its share of the flow. So it looks like your system just needs balancing.
If you now open TRV's ,and close all lockshields ( leave the rad that's heating up in its current state) and take each new rad in turn and open it's lockshield very slightly ,until it heats up. Then move onto the next rad.