Hi folks was on here last month whilst I was away from home trying to figure out what was happening with my boiler.
Basically the system pressure was fluctuation between 0-0.5 bar to 2 bar, I've just got back and checked the Schrader valve on the top of the expansion vessel and got air, practically nothing but no water so am I right in saying the vessel looks sound?
I just popped a little air in there with the heating off and brought the pressure upto 0.5 bar cold and fired up the system which brought it upto 2 bar it's dropping off again so I presume the acid test would be to flatten the water side and charge the vessel to 0.5 bar then refill the heating loop and see how it fluctuates?
Thanks in advance
Basically the system pressure was fluctuation between 0-0.5 bar to 2 bar, I've just got back and checked the Schrader valve on the top of the expansion vessel and got air, practically nothing but no water so am I right in saying the vessel looks sound?
I just popped a little air in there with the heating off and brought the pressure upto 0.5 bar cold and fired up the system which brought it upto 2 bar it's dropping off again so I presume the acid test would be to flatten the water side and charge the vessel to 0.5 bar then refill the heating loop and see how it fluctuates?