Baxi 105HE Combi - No Hot Water

Discussion in 'Plumbing and Central Heating' started by Midlandshome, 2 Apr 2020.

  1. Midlandshome

    Midlandshome

    Joined:
    2 Apr 2020
    Messages:
    6
    Thanks Received:
    2
    Country:
    United Kingdom
    Morning all, hope you're all keeping well & safe!

    I have a problem with my combi boiler, hopefully somebody can nudge me in the right direction.

    Central Heating works fine, rads are up to correct temp.

    Only get hot water when the central heating is on, otherwise it's luke-warm. No flashing lights on the boiler. When CH is on, 80 degree light is lit, when a hot tap is opened, the temp drops down to 30 degrees within a few seconds.

    If I switch the boiler to HW only mode, HW flows freely.

    I've had the cover off, no signs of water leaking from the diverter valve. The 2 pins in the DV come out when HW is called for.

    I should also say that when in 'dual mode' & the CH is off, the pilot lights for 5 or so seconds, then goes out when i call for HW (seen with cover off) if that helps?

    Any ideas please?

    Thanks!
     
  2. Sponsored Links
  3. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,377
    Thanks Received:
    2,191
    Location:
    North
    Country:
    United Kingdom
    I would say the 3 way valve has a fault, as you’re getting hot water with the heating on. I think you can get a service kit for these.
     
  4. Midlandshome

    Midlandshome

    Joined:
    2 Apr 2020
    Messages:
    6
    Thanks Received:
    2
    Country:
    United Kingdom
    Thanks! Is that another name for the diverter valve? Is this not used when putting the boiler in to HW mode only? As this provides HW as normal.
     
  5. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,377
    Thanks Received:
    2,191
    Location:
    North
    Country:
    United Kingdom
    yes it’s another name for a diverter valve (not sure if yours is pressure differential). The bit I’ve highlighted in bold - I thought you said no hot water? If this has failed, then, the heated water will not be sent around the plate heat exchanger.
     
  6. Midlandshome

    Midlandshome

    Joined:
    2 Apr 2020
    Messages:
    6
    Thanks Received:
    2
    Country:
    United Kingdom
    Sorry, my fault, I can see why the title would be misleading!

    I have no hot water when the boiler is set to HW/CH mode & CH is off.

    I have hot water when the boiler is set to HW only mode.

    I have hot water when the CH is on & the boiler is in CH/HW mode.

    Thanks again!
     
  7. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,377
    Thanks Received:
    2,191
    Location:
    North
    Country:
    United Kingdom
    Strange how you have hot water in hot water only mode, but I’m still leaning towards the 3 way/diverter, as if it’s stuck, it will still give you hot water in hot water only, however it would also heat up a rad or 2. Also have you had any work carried out recently, eg any wiring or new room thermostat?
     
    Last edited: 3 Apr 2020
  8. Midlandshome

    Midlandshome

    Joined:
    2 Apr 2020
    Messages:
    6
    Thanks Received:
    2
    Country:
    United Kingdom
    No work carried out at all. I've got a maintenance kit for the diverter valve coming today, I've seen a YouTube takedown video, apparently it can become full of 'crud' which can cause problems, so I'll try taking the whole thing out & giving it a clean. If that doesn't work, I'll call out a professional!

    Thanks for the help!
     
    • Thanks Thanks x 1
  9. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,377
    Thanks Received:
    2,191
    Location:
    North
    Country:
    United Kingdom
    Good stuff,

    Can you report back when you have an answer? It’ll help me (make sure I’m correct) and anyone else :cool:
     
  10. Sponsored Links
  11. Before you start all that,is the pin on the front of the divertor moving in and out,and switching demand light on ok,when you run a hot tap?
     
  12. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,377
    Thanks Received:
    2,191
    Location:
    North
    Country:
    United Kingdom
    I think OP stated it does.
     
    • Like Like x 1
  13. Oh yes,thanks
     
    • Like Like x 1
  14. Midlandshome

    Midlandshome

    Joined:
    2 Apr 2020
    Messages:
    6
    Thanks Received:
    2
    Country:
    United Kingdom
    Yes, both pins come out and make contact when the hit tap is run, they also go back when it’s off.
     
    • Like Like x 1
  15. Midlandshome

    Midlandshome

    Joined:
    2 Apr 2020
    Messages:
    6
    Thanks Received:
    2
    Country:
    United Kingdom
    Of course! I appreciate you taking the time to give some advice!

    As of today, in Hot Water only mode, I no longer get and HW, so the only way I get it now is if the CH has been on.

    Don’t know if this makes it easier to diagnose or harder?!
     
    • Thanks Thanks x 1
  16. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,377
    Thanks Received:
    2,191
    Location:
    North
    Country:
    United Kingdom
    I’d say it probably confirms the issue of the 3 way/diverter.
     
  17. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page