azim said:Could you indicate how i do this using the picture provided below .
Please remember , i need a idiots guide to adjusting & checking proceedure
Job for an RGI (Corgi) I'm afraid.
azim said:Could you indicate how i do this using the picture provided below .
Please remember , i need a idiots guide to adjusting & checking proceedure
azim said:Ive been qouted over the phone by Baxi themselves wait for it....... £279 .Thats over the phone ,without any inspection ,
baxpoti said:The boiler is fitted with two diagnostic indicator lights that indicate the status of the boiler. The high rate LED (yellow) can be seen through the top of the control box. The indicator LED can be seen through the front. Their sequence of operation is as follows:-
a) No power-no lights.
b) Switched live supplied indicator LED - orange.
c) Pilot established indicator LED - green.
d) Boiler fault - indicator LED red or flashing red.
e) Boiler firing at maximum rate - high rate LED - yellow.
f) Diagnostic indicator - high rate LED flashing yellow.
If the indicator LED light is illuminated red/or flashing red, it is necessary to reset the appliance. To do this turn the boiler thermostat control knob fully anti-clockwise to the OFF position and wait until the light shows
orange. Turn the control knob clockwise to the required setting. The boiler will commence the ignition sequence.
Operate the burner, this will run at low rate (This is factory set and no adjustment is necessary). Make further checks for leaks. Press and release the rate switch on the front of the control box. The high rate LED should illuminate yellow and the boiler fire at high rate (NOTE: The boiler will only run at high rate if the boiler temperature is less than 70 °C.
Check the burner setting pressure, adjusting if necessary, this has to be done while the LED is illuminated. This is done by removing the governor cover screw and adjusting the governor in either direction as required:- clockwise to increase, anticlockwise to decrease.
Soggy_weetabix said:Bit of a contradition then Baxpoti?
David