New to all this forum stuff but my aged parents had a chap round today to fix their boiler and well he didnt. he said the wiring was badly done but its worked ok for the last 2-3 years so thing he was making excuses not to bother being christmas eve and all.
Looking at the guidance I have copied and pasted the content with my bits added hope this is what is needed.
1) Boiler make / model (gas or oil)
Baxi solo 2 mains gas
2) What is / is not happening.
The power led lights up but it doesnt run
3) Has ANYTHING else been done or changed recently.
Had a new gas valve a month ago
4) When did the problem start?
few days ago
5) When does it happen? eg, heating coming on or going off.
when trying to turn the heating on nothing happens other than power led the fan does not run the pump runs but thats it. I wired the fan up in the garage to a mains supply and that ran ok so presume its not that
6) Anything else you feel may be of relevance.
Read in the forums that it may be the pipes are blocked to the pressure thingy (technical eh?) can i just remove and blow them through? are the special silicone heat proof stuff or can i use any old suitable bore pipe?
ran through the flowchart in the manual and checked the potentiometer which registered the correct values on the multimeter and suspect the pcb is at fault. Read another entry where a chap had repaired his is this something that is checkable as i dont have a clue about electronics but am quite competent at soldering. any help gratefully accepted as the old folks are moaning that they want to come and stay until its fixed
7)Please remember we are only seeing what you type and not the job !!
not sure what else i can put?
Looking at the guidance I have copied and pasted the content with my bits added hope this is what is needed.
1) Boiler make / model (gas or oil)
Baxi solo 2 mains gas
2) What is / is not happening.
The power led lights up but it doesnt run
3) Has ANYTHING else been done or changed recently.
Had a new gas valve a month ago
4) When did the problem start?
few days ago
5) When does it happen? eg, heating coming on or going off.
when trying to turn the heating on nothing happens other than power led the fan does not run the pump runs but thats it. I wired the fan up in the garage to a mains supply and that ran ok so presume its not that
6) Anything else you feel may be of relevance.
Read in the forums that it may be the pipes are blocked to the pressure thingy (technical eh?) can i just remove and blow them through? are the special silicone heat proof stuff or can i use any old suitable bore pipe?
ran through the flowchart in the manual and checked the potentiometer which registered the correct values on the multimeter and suspect the pcb is at fault. Read another entry where a chap had repaired his is this something that is checkable as i dont have a clue about electronics but am quite competent at soldering. any help gratefully accepted as the old folks are moaning that they want to come and stay until its fixed
7)Please remember we are only seeing what you type and not the job !!
not sure what else i can put?