baxi solo2 wont fire

Joined
27 Feb 2007
Messages
21
Reaction score
0
Country
United Kingdom
Hi all,

Hopefully I can explain my problem.

We have a Baxi solo2 RS boiler. This morning it hadn’t fired up(has happened before). A while ago it wouldn’t fire up and kept tripping out. When it attempted to fire up, there was a lot of clicking noises coming from the boiler sometimes firing up, but some times after a while the reset button would trip out and pilot light go out. After a lot of process I thought I had narrowed it down to the CH valve. The small little micro switch was lose, it hadn’t been switching on and off probably and had shorted out. I replaced this and every thing has been great. This was about 6 to 8 months ago.

Apart from this morning. No heating or hot water, boiler gone out and reset button tripped. I re-fired it up and the clicking/switching noise has come back. I have checked the micro switch in the valve but this is tightly done up.

Any ideas or advice??
Sorry for the length of post hope it makes sense
 
Sponsored Links
I guess there is no way of testing this to be sure is there. Just have to bite the bullet and fit one i guess
 
Any ideas for testing to see if the pcb i shot? Started OK yesterday but not today....arr
O and as far as i can tell it only dose this when demand for CH and not HW
 
Sponsored Links
Boiler doen't know whether it is on for CH or DHW.

Recheck the valves and external controls before buying a pcb.
 
Reset on an RS is overheat.

Check the system bypass and installation as per M.I.
 