RESULTS OF BALANCING
Before I started, the lockshield valves were all very different settings - a couple pretty much fully open (5 turns or so).
After 4 rounds, the rads felt pretty close in temperature. I was surprised that I did not have to open them far - the least was only set at the initial quarter turn open. The most at one full turn open.
OTHER THINGS I FOUND OUT
The boiler can easily heat all the rads really hot really quickly - so no problem there (ie with all stats set to max).
When they are all better balanced, it all seems to heat up quicker and more evenly than before. (success!)
The boiler stat seems to work. If I set it low, the rads are cooler than if set high. Next to the stat dial it lists flow temperatures - from 1 = 54 deg C to 6 = 82 deg C.
I borrowed a friend's infra-red surface temperature sensor and these are the rough average rad temps for each boiler setting I tried:
Setting 1 (flow 54C) rads at 49C
Setting 3 (flow 66C) rads at 56C
Setting 6 (flow 82C) rads at 69C
At 69C average, the individual rads were +/-7C from this.
QUESTIONS
1. Would you expect only to have the small openings of lockshield valves that I have?
2. Given the flow and rad temps I can get with the boiler, what would you set the boiler stat at?
3. Now I can measure temperatures of the rads, how close together in temp should I aim to get them (now +/-7C) if I re-balance?
4. One rad has a stuck (corroded) lock shield valve - it is the first in the flow - do I need to get this valve changed?
5. One rad seems to have the TRV on the outlet, not the inlet (found as a felt the first hot water circulate) is this a problem?
Thanks again.
QUESTIONS
Thanks again.