    Hello chaps. Got called round to a friend's house today after complaining of knocking sounds coming from the boiler. I wasn't expecting to be able to do anything about it, but said I'd have a look anyway and see if it was anything simple.

    Before arriving I had assumed it would be down to circulation problems. The boiler (WB Greenstar 42CDi) had a new plate HEX fitted within the first year due to becoming blocked on the primary/heating circuit side. I mains flushed and inhibited the system last year, but it's possible that the main heat exchanger is filled with crud that the flushing didn't release.

    In any case, got there to find that the condensate neutraliser had become blocked, and the condensate wasn't able to syphon away properly. Have removed the neutraliser until Plumb Centre get a replacement through from another branch, and the boiler seems to be working just fine now. Even tried closing down all rad valves to leave circulation through the bypass only in an attempt to try and reduce circulation and see if the knocking started again, but it never came back.

    Is this pure coincidence that the problem went away and that it's likely to come back, or can a blocked condensate drain really cause boiler knocking/banging/kettling?
     
  2. Sponsored Links
  3. Nige F

    Nige F

    Joined:
    28 Jun 2005
    Messages:
    21,204
    Thanks Received:
    1,741
    Country:
    United Kingdom
    no idea M8 - but I`m pleased you`re not going to leave the neutraliser out - and pollute the Fens ;)
     
  4. Bankrupt

    Bankrupt

    Joined:
    6 Aug 2009
    Messages:
    387
    Thanks Received:
    26
    Location:
    Warwickshire
    Country:
    United Kingdom
    I can assure you that a blocked condensate drain will cause exactly what you describe on this model. I have the same boiler and had exactly those symptoms when the drain froze up during the recent big freeze.
     
    • Thanks Thanks x 1
  5. electronicsuk

    electronicsuk

    Joined:
    7 May 2007
    Messages:
    3,316
    Thanks Received:
    275
    Location:
    Lincolnshire
    Country:
    United Kingdom
    Well I'm sure he'll be pleased to learn that there probably isn't another fault, as I wasn't happy to declare the all-clear when I left it. Thanks guys.

    I'd be more worried about damage the the (very old) bricks the house is constructed from around the area of the condensate drain ;)
     
  6. simond

    simond

    Joined:
    26 Oct 2004
    Messages:
    5,232
    Thanks Received:
    465
    Location:
    Surrey
    Country:
    United Kingdom
    This condensate stuff is virtually harmless. It is a load of hot air with a small smattering of carbonic acid.

    Add a slice of lemon, delicious :LOL:
     
  7. Bankrupt

    Bankrupt

    Joined:
    6 Aug 2009
    Messages:
    387
    Thanks Received:
    26
    Location:
    Warwickshire
    Country:
    United Kingdom
    Indeed - I've heard it described on this forum as being "highly acidic" . :rolleyes: It's not highly acidic (something like concentrated nitric acid is highly acidic) , it's very slightly acidic......
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page