Sounds like the safest thing would be to not dissuade him from having an 8.5kW load on a 5A fuse...
and if the tenant that fries is asian aswell then that'll be alright will it?dingbat said:securespark said:Dingbat-
I see this all the time...
Trouble is it's not just the cowboys it's the customers as well. I'm going out shortly to try and convince a potential client that running a (8.5kW)shower off a five-amp BS3036 fuse is simply not going to work. Having seen another of his houses (oh no, Asian landlord alert) I just know, from what he's said, that there will be absolutely no bonding anywhere and probably an undersized main earth conductor. Chances are there will be many additional sockets, added willy-nilly and he will have put in multiple-lamp luminaires everywhere, downlighters and all kinds of sh*t. As for RCD's...
He's a real tightwad and I don't expect he'll accept my quote for doing it right. I'm taking a copy of the regs with me this time, along with some information about the forthcoming changes to building regs and a reminder of his obligations to his tenants.
You know, I almost hope he turns me down then one of his tenants fries in the shower... (Sorry, but, you know what it's like sometimes!)
plugwash said:well the niceic said that 2x2.5mm cable runs from a 32A breaker too distant fcus was fine
only SHORT CUIRCUIT protection has to be at the start of the cable
overcurrent protection can be at the destination end
this is what the recs do with service cables and is perfectly safe