stulew said:
The main fuse is a 3 Amp... What is the best and most methodical way to eliminate the parts of the boiler that require a feed from the mains. I have put different demands, H/W and C/H on it and it stilll blows. I take it I should test the fan etc with a meter but what is the right sequence etc.
Any Help would be greatly appreciated.
Many Thanks
When you say 'conventional boiler', I am assuming you mean a old bog standard boiler, without the all-singing-all-dancing features of modern combi- or system-boilers.
Anyway, in old boilers, the only parts that make demands on the electric, are the pump, the 3way valve, and the gas valve.
(I would be curious to know why you have a three-way valve in a gravity fed system)
You can see that these parts are used in any 'demand' situation, although if it is gravity fed, when using H/W you can eliminate the pump from the equation.
So basically you are looking at either the 3way valve, or the gas valve.
We have eliminated the 3way valve, because its new. (Unless your problems started when it was replaced, duh!)
So it might be a dodgy gas valve.
And 3amp fuse sounds a bit low, are you sure it doesnt just need 5amp.
I had a 'conventional' boiler at one point, it wasnt too big, but it drew 5amps (i.e. it had a 5amp fuse, not it actually drew 5amps).