hi all,
thanks for the comments.
i was very gentle with the aps, didnt disconnect it, only removed the air hose from the venturi and gently, very very gently blew into it to see if it was stuck open as someone said it might be.
where i am at present is i think the pcb is at fault. i have disregarded what the plumber said as i think it is biasing my fault finding. i got the fault finder diagram from the si and started from scratch.
I ignored all the gas checks as i dont really want to be messing with any of that side of it and concentrated on the electrics, whilst fault finding i found the following to be true, there is 240v at the switched live from the programmer. There is 240v at the 3 way switch and then from there at the hi and low thermostats, the thermostats are both fine with 240v back to earth at both terminals. there is 240v at the pcb live connection, there is nothing at the fan terminals. i have checked the wiring flow diagram and also traced the wires through the boiler and on the back of the pcb to see what is in sequence for the ignition to happen.
i think it is as follows, call for heat comes, 240v goes to boiler over heat stat, switch is closed if boiler is not over heating, then next inline is the fan, fan spins up and thus closes the aps, this switch then sends 240v back to the pcb which then goes to the ignition side of the pcb and the boiler ignites.
in my boiler when the call for heat comes the boiler over heat stat does not have 240v across or at either terminal. i have tested and the stat is ok. The pcb circuit board does not have 240v across or at either of the boiler over heat stat points. therefore i think there is some fault in the pcb in relation to the boiler over heat stat part of the sequence.
to test my theory i put 240v to the boiler overheat stat and the boiler fired up.
I have ordered a replacement pcb, i thought it cant hurt to spend £120 to try and save £1600.
i will report back how i get on.