Boiler Replacement

Joined
1 Dec 2006
Messages
8,322
Reaction score
1,338
Location
Cumbria
Country
United Kingdom
After another breakdown I have decided it might be time to replace our 16 year old Ideal Logic 35.
In order to get an idea of the costs I tried a couple of these online pricing sites.
They ask various questions but one that I would like some help on is the number of radiators. Do double radiators count as a single radiator or two for the purpose of assessing the correct boiler size. Thanks
 
Just one, it is only an indication of what size boiler is required, it isn't exact.
 
replace it for another logic be a doddle of a job as all pipes and flue hole should line up saving you labour costs
Get someone local through recommendation from family /friends
 
A proper heat loss calculation determines the correct boiler size, and that can only be done with a site visit. Assuming you're in England or Wales, it's been part of Building Regulations to do this for a boiler replacement. The online sites won't care whether it's a single or double, they'll be taking a finger in the wind average, making assumptions that you will have some of each
 
A proper heat loss calculation determines the correct boiler size, and that can only be done with a site visit. Assuming you're in England or Wales, it's been part of Building Regulations to do this for a boiler replacement. The online sites won't care whether it's a single or double, they'll be taking a finger in the wind average, making assumptions that you will have some of each
LOGIC 35 so a combi so will be sized for HW on a like for like 35 it drops down to 7.5kw the 30 drops to 6.4kw
 
Last edited:
After another breakdown I have decided it might be time to replace our 16 year old Ideal Logic 35.
In order to get an idea of the costs I tried a couple of these online pricing sites.
They ask various questions but one that I would like some help on is the number of radiators. Do double radiators count as a single radiator or two for the purpose of assessing the correct boiler size. Thanks
Is there any reason to think a replacement with similar output to the existing wouldn't be OK?
 
New build house builders love throwing in Logic ESP 35 boilers, they must get them dirt cheap from Ideal.
Half the time, they're grossly overpowered for the house.
 
Is there any reason to think a replacement with similar output to the existing wouldn't be OK?
When the boiler was installed we had a large cast iron roll top bath that took too long to fill from the boiler that was in when we bought the property. The Logic 35 gave 17L/Min and was much quicker for running a bath. I always felt it was a bit overpowered but wanted the convenience. I will get proper size calculations done before I order the replacement.The online pring sites suggested that 30KW boiler would be adequate but I wasn't sure if the majority of the radiators being doubles would make a different result
 
When the boiler was installed we had a large cast iron roll top bath that took too long to fill from the boiler that was in when we bought the property. The Logic 35 gave 17L/Min and was much quicker for running a bath. I always felt it was a bit overpowered but wanted the convenience. I will get proper size calculations done before I order the replacement.The online pring sites suggested that 30KW boiler would be adequate but I wasn't sure if the majority of the radiators being doubles would make a different result
ideal logic 30kw will give you about 12.4 litres per minute a 24 will give you 9.9 litres the 35 gives 14.5 litres
Hw delivery is your first consideration when going for a combi
 
A three bedroom semi built in the 30's with solid walls, double glazing throughout, 200mm insulation in the loft and an uninsulated suspended ground floor is likely to have a heating loss of around 8kW at -3°C so your concern with heating is how low can the boiler go not how high. The higher power is for hot water flow (if you have a main that can deliver an appropriate supply of cold water).

A boiler that modulates to below 3kW, preferably 2kW would be suited well as the weather is rarely -3°C, more likely 6-10°C so the boiler that can't modulate below 6kW will be cycling a lot.
 
ideal logic 30kw will give you about 12.4 litres per minute a 24 will give you 9.9 litres the 35 gives 14.5 litres
Hw delivery is your first consideration when going for a combi
Now I only have a shower I assume 12.4 litres/min would be ample, as they claim it will be for a shower.
 
A three bedroom semi built in the 30's with solid walls, double glazing throughout, 200mm insulation in the loft and an uninsulated suspended ground floor is likely to have a heating loss of around 8kW at -3°C so your concern with heating is how low can the boiler go not how high. The higher power is for hot water flow (if you have a main that can deliver an appropriate supply of cold water).

A boiler that modulates to below 3kW, preferably 2kW would be suited well as the weather is rarely -3°C, more likely 6-10°C so the boiler that can't modulate below 6kW will be cycling a lot.
That pretty much describes our house except that we have uninsulated cavity walls so I guess the heat loss would be similar. Would you know or can you tell me how to find out the figures for modulation for a 30KW Ideal boiler.
 
That pretty much describes our house except that we have uninsulated cavity walls so I guess the heat loss would be similar. Would you know or can you tell me how to find out the figures for modulation for a 30KW Ideal boiler.
i gave the figure for the 30kw on post 5
 