Eight, possibly ten, 1mm ² twin and earths from a switch panel to eight, possiby ten, lamps 50 metres away. The switch panel is fed from a fused switched outlet so the total current in the bunched cables is limited to 6 amps. ( accepting there will be short duration overload in fault conditions till the fuse blows ).
Guides and cable size selection require the cables to be 1.5 mm²
Common sense appears to suggest that 1 mm² is adequate. If only one cable is taking the full 6 amps then the others will have no current and therefor not contributing anything to the derating equation. That situation will not happen as largest lamp will be 100 watts
This is going to come up between a jobsworth electrician and a money conscious client.
Guides and cable size selection require the cables to be 1.5 mm²
Common sense appears to suggest that 1 mm² is adequate. If only one cable is taking the full 6 amps then the others will have no current and therefor not contributing anything to the derating equation. That situation will not happen as largest lamp will be 100 watts
This is going to come up between a jobsworth electrician and a money conscious client.