My combi boiler is 13 years old
Still don't.You mention "bigger rads" but we don't know how big your old ones are.
No harm to compare some numbers,
If you have a rad with flow/return temps of 65C/50C then the rad will output 68.8% of its rated output.
If the rad has flow/return temps of 45C/40C then that rad will output 35.4% of its rated output or 51.4% of the 65C/50C output.
I'm betting on the Goverment forcing up the price of gas to make people change