C&G 2391

You maybe need to be a member to be able to view the documents?? I have sent you an email address for rocknroll who set the site up.
 
I have tried everything (inc password) to join Sparky Heaven, without success. Would it be possible for someone to send me any C&G 2391 past papers. I sit mine in July, I'm really desperate
 
ColJack said:
one or 2 questions i was not 100 sure of..

1. for a T-N-S system, calculate the maximum permisable Zs of a 30mA rcd.. ( no other info given.. )

i worked it out ( after an epiphany at 1:50.. good job I sat there... ) that it was 50/30mA = 1666 ohms... this sounds high for me but is ok to the regs for dry locations on TT systems..
can't find the formula for T-N-S systems though.

Your right om the 1666 ohms but some say `but no more than 200 ohms`
Whether its a T.T, TNC-S or a TNS the max Zs is the same, so for C&G to mention TNS system their just trying to be foxy!!!
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top