HI
In a IT suite at a local school we have dado tunking with Cat5 and power in it. The sockets are wired on 20amp radials 3 or 4 sockets on each trip. They are wired in 2.5mm Low smoke single. We have had some sockets moved and they have been wired from the first socket on the radial (Low smoke connecting this socket to distrbution board) in 2.5mm T&E with a 4mm bond cable between earth terminals on the new sockets.Am I right in thinking this wrong and should have been done in low smoke cable or is it going to be ok.
Also as some of the sockets in the trunking are on different trips should the earth terminals of the sockets all be bonded together.
Thanks
Carl
In a IT suite at a local school we have dado tunking with Cat5 and power in it. The sockets are wired on 20amp radials 3 or 4 sockets on each trip. They are wired in 2.5mm Low smoke single. We have had some sockets moved and they have been wired from the first socket on the radial (Low smoke connecting this socket to distrbution board) in 2.5mm T&E with a 4mm bond cable between earth terminals on the new sockets.Am I right in thinking this wrong and should have been done in low smoke cable or is it going to be ok.