Cable sizing a shower

Joined
10 Feb 2007
Messages
1,389
Reaction score
40
Location
Cumbria
Country
United Kingdom
9kw shower
30m cable length
SWA
Clipped direct outdoors uncovered
What would the CSA be on the cable?
Cheers in advance
 
Sponsored Links
9kW @ 240V = 37.5A
so 40A MCB.
so 4mm. SWA clipped or buried in masonry.

You might care to use 6mm² to cover a larger shower.
 
Sponsored Links
First time I have ever heard someone suggest 6mm for a 9kw shower.
And like the other poster implied, 4mm sounds extremely light for drawing all those amps?
It was 30 metres, not 30 centimetres.
 
First time I have ever heard someone suggest 6mm for a 9kw shower.
And like the other poster implied, 4mm sounds extremely light for drawing all those amps?
It was 30 metres, not 30 centimetres.
Well do the sums rather than relying on instinct. Cable type and installation method are more important than you might think
 
First time I have ever heard someone suggest 6mm for a 9kw shower.
You need to get out more.

I suggested 4mm².

9kW @ 240V is 37.5A
4mm² SWA has a Method C CCC of 42A, and
6mm² 53A
10mm² 73A

And like the other poster implied, 4mm sounds extremely light for drawing all those amps?
It was 30 metres, not 30 centimetres.

If it sounds wrong, you are listening to the wrong things.
upload_2020-1-28_16-26-20.png
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top