    Would it be ok to run two cables for a ring main in with CH pipes as follows.
    Total ring board to board 2.5mm T&E, 36m fixed method 1 within a boxing 200mm x 50mm x2400mm containing 22mm CH flow and return and domestic water 15mm Hot and cold.
    obviously can keep cables adjacent to cold water pipe and CH pipes furthest away.

    Any issues with that?
    Thanks in advance
    Gareth
     
  2. Sponsored Links
  3. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    What will be the maximum temperature inside the boxed-in section?
     
  4. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,627
    Thanks Received:
    2,382
    Location:
    Londonderry
    Country:
    United Kingdom
    Could you go in to a little more detail regarding installation method 1?
     
  5. chappers

    chappers

    Joined:
    27 Aug 2004
    Messages:
    3,254
    Thanks Received:
    357
    Country:
    United Kingdom
    Interesting re the temp, central heating pipes carrying water at 65 degrees, maybe high 40s-50s, that was my primary concern.
    As for method 1, just clipped to the wall inside the boxing. It's probably got some new designation nowadays
     
  6. Iggifer

    Iggifer

    Joined:
    8 Sep 2011
    Messages:
    4,637
    Thanks Received:
    587
    Location:
    Warwickshire
    Country:
    United Kingdom
    It's reference method C
     
  7. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    73,410
    Thanks Received:
    4,226
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    climaflex or similar insulation on the pipes will reduce the air temperature inside the enclosure, and also prevent the cables coming into contact with hot pipes.

    lag the pipes first, then measure the temperature. It may affect current capacity of the cable, more so if it is for an immersion heater or electric shower which draws high current for an extended period.

    PVC cables can soften and deform badly if they are pressed against hot pipes (this often happens when they are poked into a notched joist together and a floorboard nailed on top).
     
  8. Sponsored Links
  9. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,627
    Thanks Received:
    2,382
    Location:
    Londonderry
    Country:
    United Kingdom
    Clipped direct is reference method C (has been for some time).
    The issue is the build up of heat and that current carrying cable will not be able to dissipate heat satisfactory. So the best thing would be to either, reduce the heat in the enclosed boxing, separate the cables be sectioning off, or increase the cable CSA.
     
  10. chappers

    chappers

    Joined:
    27 Aug 2004
    Messages:
    3,254
    Thanks Received:
    357
    Country:
    United Kingdom
    Thanks for the replies, the current central heating pipes are already in a box following the route and I dangled a temp probe down there over the weekend and it peaked out at 39 degrees.
    I think I will do as above and section the boxing off and insulate around the pipes.
    I realise it's not the deciding factor, but there will only be 4 double sockets on the whole ring as it's for a loft conversion
     
  11. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    At whatever the CCC is for a cable given its size and installation method etc, the conductor will be at 70°.
     
  12. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    Only at the ambient temperature that was used to determine that CCC - usually IIRC 25 deg Celsius.
     
  13. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Ah - "etc" in "given its size and installation method etc" was meant to cover all the derating factors which apply.
     
  14. chappers

    chappers

    Joined:
    27 Aug 2004
    Messages:
    3,254
    Thanks Received:
    357
    Country:
    United Kingdom
    Just to update, separated the central heating pipes from the rest of the boxing with a bit of 2x1 and redid the temperature probe thing. this time it peaked out at 28 degrees, so combined with a bit of insulation around the CH pipes I think I'm happy to go with that.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page