i have recently bought i replacement hob and cooker for my kitchen. The supply cable i have in already is a 6mm twin & earth fed from a 32A breaker, with a 45A cooker iso located in the kitchen
The new hob i have bought is rated at 7.4kW and the new cooker is rated at 3kW.
Now together i have these rated to pull just over 43A how can i go about hard wiring in these to appliances together??
Is the cable size and breakers suitable?