For a radiator that size you average electric 500 watt element would not heat it effectively and it would certainly not heat your room. The heatloss from the rad would be about 2kw so you would need to stick a 2kw element in it. These require a minimum 2" boss which you don't have
Forget this one it is not really feasable. If you do decide to give it a go put a safety valve (even a spring loaded one) on the top
To pick up on boilermans post, can you not remember the old oil filled electric radiators from the 70's 80's. That is why they were oil filled.
Forget this one it is not really feasable. If you do decide to give it a go put a safety valve (even a spring loaded one) on the top
To pick up on boilermans post, can you not remember the old oil filled electric radiators from the 70's 80's. That is why they were oil filled.