    I have an internal wall separating two rooms where the wall between the room supports the upstairs floor joists and a a dividing wall between two bedrooms upstairs.
    My question is that i am creating a 1500mm opening between the two rooms downstairs and i am fitting a 1950mm heavy duty catnic box lintel for support the wall is block built and the overlap of the lintel each side to rest on the remaining wall is going to be 225mm. Could you tell me whether i would need to use padstones on this width of opening and with the additional width of lintel used.
    Thanks
     
  2. Sponsored Links
  3. Roger Wales

    Roger Wales

    Joined:
    10 Jul 2021
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    This is the lintel used:
    Catnic BHD100 Box Lintel 1950mm
     
  4. Bouy

    Bouy

    Joined:
    20 Mar 2019
    Messages:
    106
    Thanks Received:
    19
    Country:
    United Kingdom
    No, padstones not required on lintels. To put it into perspective, with the maximum load of 39kn load allowed on your lintel the load placed on your supporting walls would be less than 1.3N/mm2, I would imagine your wall blocks will have a crushing strength of at least 3.5N/mm2
     
  5. Roger Wales

    Roger Wales

    Joined:
    10 Jul 2021
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    I have ripped the coverings of what has been done and to show a pic of bricks wall is made of and box lintel used. So are you saying with an loading point width either side of 185mm is suffice.?
     

    Attached Files:

  6. tony1851

    tony1851

    Joined:
    23 Feb 2012
    Messages:
    10,406
    Thanks Received:
    1,574
    Location:
    Manchester
    Country:
    United Kingdom
    With a max. reaction of 19kn (unfactored?) bearing stress would be 19x1000/250 x 100 = 0.76N/mm2, so agreed he wouldn't need padstones.
     
  7. Sponsored Links
  8. Roger Wales

    Roger Wales

    Joined:
    10 Jul 2021
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    Thank you very much for your assistance, am a new user and very impressed with fast response here.
     
  9. Bouy

    Bouy

    Joined:
    20 Mar 2019
    Messages:
    106
    Thanks Received:
    19
    Country:
    United Kingdom
    Yes as stated even using standard 150 bearing length, 19.5 x 1000 /150 x100 = 1.3N/mm2
     
  10. Roger Wales

    Roger Wales

    Joined:
    10 Jul 2021
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    Thank you
     
  11. Nakajo

    Nakajo

    Joined:
    5 Dec 2014
    Messages:
    2,094
    Thanks Received:
    195
    Location:
    Berkshire
    Country:
    United Kingdom
    We pride ourselves on speed over accuracy.
     
    • Like Like x 2
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page