CCC of 1.5 T & E

Joined
11 Jan 2004
Messages
45,987
Reaction score
3,560
Country
United Kingdom
Could someone look in their 16th Brown & tell me what the CCC is of 1.5 T & E Method 1, please?

For reasons I will not elaborate on (!), I cannot get mine out of the van!
 
20A in my book (OSG) for clipped direct

Sounds a bit high when you say it quickly :shock: lol (but I suppose thats becuase clipped direct doesn't occur in houses too often)

15.5 for one and 27 for two and a half for what its worth, four is 37 and six is 47 and a whole 65 on ten
 
Cheers, Adam! Thanks very much!

Mods. Can you delete this now? I only wanted an answer to this question.
______________________
Lynda, moderator

seems you got more than you asked for.

If you still want it removed email me
 
Adam_151 said:
20A in my book (OSG) for clipped direct

Sounds a bit high when you say it quickly :shock: lol (but I suppose thats becuase clipped direct doesn't occur in houses too often)

15.5 for one and 27 for two and a half for what its worth, four is 37 and six is 47 and a whole 65 on ten

I've never really thought about it before, but seeing it written out like that shows clearly that as the cable gets bigger, the allowed current density in the conductor gets smaller - at 10mm it's less than half that at 1mm (6.5 and 15.5 Amps/sqmm respectively). I suppose it must be the problem of heat dissipation, because it can't be the resistance! :)

Cheers,

Howard
 
HDRW said:
Adam_151 said:
20A in my book (OSG) for clipped direct

Sounds a bit high when you say it quickly :shock: lol (but I suppose thats becuase clipped direct doesn't occur in houses too often)

15.5 for one and 27 for two and a half for what its worth, four is 37 and six is 47 and a whole 65 on ten

I've never really thought about it before, but seeing it written out like that shows clearly that as the cable gets bigger, the allowed current density in the conductor gets smaller - at 10mm it's less than half that at 1mm (6.5 and 15.5 Amps/sqmm respectively). I suppose it must be the problem of heat dissipation, because it can't be the resistance! :)

Cheers,

Howard

The strands get bigger too though dont they? So smaller surface area. I know its the voltage that goes round the outside of a cable..but maybe it still has an effect?
 
skin affect is negligable at 50hz on domestic sized cables (it *is* an issue on some big distribution cables though)

its because CSA goes up proportional to r² but the circumfrance (which is equivilent to the surface area of the cable as a whole per unit length, surfaces of strands that touch each other don't count) goes up proportional to r.

and its the circumfrance (as well as the insulation and what the cable is burried in) that sets current carrying capacity.

this is why on the really big overhead powerlines you see conductors in groups, each conductor can cool seperately but there is still only one insulator needed to hang the whole group.
 
securespark said:
For reasons I will not elaborate on (!), I cannot get mine out of the van!

OK, I'll go first.

Have you forgotten where you parked your van in a multi storey?
 
Locked your keys in the back of the van?

All our vans are fitted with slam locks on the back doors, and keys often get locked in there. :oops:
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top