    Hello. Im about 90% sure I know what Im doing here, Just looking for someone to check over before I dig in.

    Im removing a Centaurplus C27 with stored hot water and fitting the Evohome setup that I had from my previous house. Old house was gas with on-demand hot water, so I have bought the hot water add on for this, Which leaves me wiring up 2 BDR91s in replacement of the old C27.

    Im pretty sure its as simple as connecting the live and earth from the C27 to both BDR91s, then C27 1&2 go to the BDR91 for heat conections B&C, C27 3&4 to the BDR91 for hot water B&C and a link L to A on both BDRs

    The honeywell system should then take care of the thermostat, however, there is a room thermostat that needs to be removed, and that part Im not sure of. I suppose I could set it on full and let the evohome do the job, but Id rather remove. Any tips? or anything I havent got right?

    Thanks in advance!
     
  2. Sponsored Links
  3. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,899
    Thanks Received:
    1,672
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Your theory is along the right lines, however, regarding:
    Are there presently wires connected to the C27 terminals 1 & 2? A connection to terminal 1 is fairly common in the UK (but not always it depends on the type of system it's connected to), but it would be extremely unusual to have a connection to terminal 2, [CH Off]

    aa.JPG
     
    • Thanks Thanks x 1
  4. somedudebob

    somedudebob

    Joined:
    26 Nov 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi.. Thanks for the reply. The C27 thats in place at the minute is working to the extent where I can turn the heating and HW on and off, Just not set timers, (screen is dead)

    Im loathed to remove it to check until Im sure what I am doing, as if it doesnt come back on, and the heating doesnt work, well.... Wife will be angry and no one needs that!
     
  5. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,094
    Thanks Received:
    10,163
    Location:
    Livingston
    Country:
    United Kingdom
    BDR91 doesnt have an earth, you might want to use a Neutral, NEVER go with wiring colours on heating sytems
     
    • Like Like x 2
    • Thanks Thanks x 1
  6. Sponsored Links
  7. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,899
    Thanks Received:
    1,672
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    With what you propose, you are connecting CH and HW control wires to the same BDR91. For example terminal 3 is a HW control wire and terminal 4 is CH control wire, yet you propose to connect them both to the BDR91 for hot water. :confused: The same is true of terminals 1 and 2 if they are actually fitted.

    The wires should be moved from the C27 to the BDR's as below:

    C27 N & L → Both BDR 91’s N & L (If using 3 core cable isolate/insulate earth wire safely)

    C27 ‘1’ → HW BDR 91 ‘C’ (if fitted)

    C27 ‘2’ → CH BDR 91 ‘C’ (if fitted - very unlikely)

    C27 ‘3’ → HW BDR 91 ‘B’

    C27 ‘4’ → CH BDR 91 ‘B’

    Link ‘L’ to ‘A’ on HW BDR 91

    Link ‘L’ to ‘A’ on CH BDR 91

    As you have figured, the old room thermostat can't simply be disconnected as this would leave the heating wiring 'open circuit' and it would not operate, the integrity of the circuit needs to be maintained. As not all thermostats are the same, some working out will be required.

    1. Look at the wiring diagram for your make/mode of thermostat that you are removing. If you don't have the instructions for it, a diagram is usually printed inside the lid. This will show which are the two live switching wires, and which is the neutral wire. (If there is a neutral present. Not all thermostats need or have one fitted)

    2. Trace the thermostat cable back to its origin.

    3. Take take a photo, or make a note of where the live switching wires are connected at their origin.

    4. You can now disconnect all of the wires going to the old thermostat and remove the cable and thermostat.

    5. Insert a wire link between the terminals where the two live switching wires have just been removed from, so that they are now electrically joined together.
     
    Last edited: 26 Nov 2021
  8. somedudebob

    somedudebob

    Joined:
    26 Nov 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Sorry, You are correct. Its even labelled N on both devices
    Yes, Well noticed. 1&3 to one BDR for HW, 2&4 to the other for CH. L to A on both

    The Room Stat is a SUNVIC TLM model, and I am assuming is wired to the boiler house (The C27 is on the other side of the house, the boiler on the other side of the wall from the Room Stat) so hopefully shouldnt be too difficult to trace. The Room Stat is also right above the radiator for that room..... Sensible.....
     
  9. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,899
    Thanks Received:
    1,672
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    tlm.JPG

    If it's this model, the live switching wires are connected to terminals 1 and 3. Trace the cable back to its origin; note where the wires that go to 1 and 3 are connected and then disconnect all of the wires in the cable going to the thermostat completely. Finally link the terminals where the wires that went to 1 and 3 have just been removed from.

    If your thermostat is different, or you need any help, post back.

    As a suggestion you could do the BDR's first & set the TLM thermostat to max to test everything is working OK. Once you know all is well, then you can decommission the TLM.
     
  10. somedudebob

    somedudebob

    Joined:
    26 Nov 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Yes. I think that is going to be my way forward, to make sure no mistakes are made along the way. Im going to need to track some cable in the wall as the BDR91s need to be 30CM apart, and need to fit some back boxes to make a nice job of this for mounting them.

    Thanks for all the help, at least I know what I need to do with wiring now, just the physical fitting to go. Luckily I have a fair amount of 240v cable lying around.
     