Hi i have a vaillnt eco tec pro 28 about 6 years old in ch mode pressure loss through prv also problem with system pressue if it falls below 1.3 bar boiler cuts out :(
 
Sponsored Links
If water is escaping out if the PRV whilst boiler is fired up then I would be checking the expansion vessel. If you're someone that knows your way round a bag of tools then you could probably recharge it yourself, otherwise you should call an engineer. If it is only a recharge that it needs as opposed to having a split diaphragm then it shouldn't cost more than £80 + vat. At least that's what I charge to re-pressurise a vessel on that boiler. It should only take a second or two to determine whether you need a new vessel or not.
 