Prof : plumb
I checked the vent pipe dimensions they are ok
Turned the pump down to speed 1 (was on 2)
Then I wondered about what you said on the possible cold feed pipe block
The supply to the tank is only a few inches from the pump isolation valve
So I bailed out the tank to see if there was much sludge it the bottom.
I then drained down the system, took the pump off, and opened the pump isolation valve and poured water in the tank after about 4 pints nothing much had appeared; I was about to put another couple of pints in when sediment and water come through the pipe,
So it appears that I had a partial blockage in the cold water supply.
I have refilled the system bled it and run it up, after a couple of hours there is no sign of the cold water tank getting hot.
Once I am sure everything is ok I will partially drain the system and add corrosion inhibiter (Don’t see the point of wasting £20 by putting it in until I am sure the heating is working ok and won’t need draining down again)
I hope that lot makes sense to you.
Many thanks for your advice