Hello to all, hope you can help.
We've an oil fueled Potterton central heating system, with two zone valves opened by Drayton ZA5 actuators, (one for CH, one for HW) and controlled by a Danfoss Lifestyle LP522 controller and Grundfoss Alpha+ pump.
In the last months and very occasionally we've noticed the downstairs radiators not getting warm, it's been intermittent but gradually got worse and in the last few days the downstairs rads have not got warm at all. The upstairs one's have always got warm as has the hot water from the taps.
The gradual pattern of failure has been rather strange in that the downstairs rads would get warm in the mornings but not get warm in the evenings - now the upstairs rads don't get warm at all when the system switches on, morning or evening.
The boiler has been serviced and given a clean bill of health and I've changed the actuator and checked the valve is easy to operate on the CH side of the system, the hot water actuator and valve works perfectly. I've also put a new Lifestyle LP522 controller on and still have the problem of downstairs rads not getting warm.
When the controller calls for everything to switch on both actuators move to their open position and the "switched on" indicator light on the pump comes on, however I can't perceive any vibration or noise from the pump to indicate it's working.
So my question is - despite it's light coming on is it likely to be the pump at fault or could it be something else ?
Many thanks.
We've an oil fueled Potterton central heating system, with two zone valves opened by Drayton ZA5 actuators, (one for CH, one for HW) and controlled by a Danfoss Lifestyle LP522 controller and Grundfoss Alpha+ pump.
In the last months and very occasionally we've noticed the downstairs radiators not getting warm, it's been intermittent but gradually got worse and in the last few days the downstairs rads have not got warm at all. The upstairs one's have always got warm as has the hot water from the taps.
The gradual pattern of failure has been rather strange in that the downstairs rads would get warm in the mornings but not get warm in the evenings - now the upstairs rads don't get warm at all when the system switches on, morning or evening.
The boiler has been serviced and given a clean bill of health and I've changed the actuator and checked the valve is easy to operate on the CH side of the system, the hot water actuator and valve works perfectly. I've also put a new Lifestyle LP522 controller on and still have the problem of downstairs rads not getting warm.
When the controller calls for everything to switch on both actuators move to their open position and the "switched on" indicator light on the pump comes on, however I can't perceive any vibration or noise from the pump to indicate it's working.
So my question is - despite it's light coming on is it likely to be the pump at fault or could it be something else ?
Many thanks.