Hi, I'm not sure whether i'm after help, advice, reassurance or all three here so bear with me.
I have an old Glow worm space saver 20-30 F boiler. A honeywell 4073a 3 port valve, honeywell cylinder stat and honeywell room stat. (y plan?)
The HW is gravity fed and CH is pumped.
If I have programmed for HW & CH to come on for 4 hours for example, the hw will come up to temp (60deg) fine BUT this will then cut out the CH. This applies even if the room stat is set at 30 deg. The CH seems to come back on again when the HW has reduced in temp sufficiently for it to called for again. It's as thought the room stat has no bearing on the CH staying on. As long as the orange light on the room stat is on the CH will come on with the HW (when both are called for). The orange will click on at approx 10/15 degrees.
From reading the forums it appears that with gravity HW & pumped CH you can only have them together but should the CH not continue as long as both are on at the programmer even though the HW has been satisfied and the room stat is set at 30? Or does it run on a cycle whereby the rads heat up/cool down in line with the HW demand?
The 3 port, cylinder stat and room stat have all been replaced from the originals (all 20+ yrs old) in the last couple of months but the result is the same.
When the HW has been satisfied the 3 port doesn't seem to move over to leave port A open. If i have programmed the HW & CH to both be on but the room stat turned right down, the HW will heat up to temp fine, then when I turn room stat on/up the pump will turn continue and the boiler will fire but the valve won't move to open port A only.
It's now got to the stage where it is annoying me because on very cold nights the house warms up a treat but will then become chilly until the HW is demanded again.
Is there a problem with the wiring or am I expecting too much from an old (22 years) system?
I have an old Glow worm space saver 20-30 F boiler. A honeywell 4073a 3 port valve, honeywell cylinder stat and honeywell room stat. (y plan?)
The HW is gravity fed and CH is pumped.
If I have programmed for HW & CH to come on for 4 hours for example, the hw will come up to temp (60deg) fine BUT this will then cut out the CH. This applies even if the room stat is set at 30 deg. The CH seems to come back on again when the HW has reduced in temp sufficiently for it to called for again. It's as thought the room stat has no bearing on the CH staying on. As long as the orange light on the room stat is on the CH will come on with the HW (when both are called for). The orange will click on at approx 10/15 degrees.
From reading the forums it appears that with gravity HW & pumped CH you can only have them together but should the CH not continue as long as both are on at the programmer even though the HW has been satisfied and the room stat is set at 30? Or does it run on a cycle whereby the rads heat up/cool down in line with the HW demand?
The 3 port, cylinder stat and room stat have all been replaced from the originals (all 20+ yrs old) in the last couple of months but the result is the same.
When the HW has been satisfied the 3 port doesn't seem to move over to leave port A open. If i have programmed the HW & CH to both be on but the room stat turned right down, the HW will heat up to temp fine, then when I turn room stat on/up the pump will turn continue and the boiler will fire but the valve won't move to open port A only.
It's now got to the stage where it is annoying me because on very cold nights the house warms up a treat but will then become chilly until the HW is demanded again.
Is there a problem with the wiring or am I expecting too much from an old (22 years) system?