I have a Drayton LP811 timeswitch which at the moment is used as one of the controllers on a standard S-Plan+, switching at mains voltage.

Could I change this to switch a 24V feed instead? The manual says it has "volt free contacts". Is it simply a matter of removing the link between L and COM and connecting a 24V feed to COM instead?

1735409367545.png
 
The (extra) low voltage wiring can be connected to the 'volt free' contacts, on terminals 1 and 3, if the link between L and 1 is removed.

Usually you wouldn't be connecting a 24V feed. You would be connecting a new cable/flex to the ELV terminals on your boiler.
However, there are a lot of mains operated controls on an S Plan+ system, so I don't know how you intend to mix the voltages. Is this related to the posts about X Plan systems?
 
The (extra) low voltage wiring can be connected to the 'volt free' contacts, on terminals 1 and 3, if the link between L and 1 is removed.

Usually you wouldn't be connecting a 24V feed. You would be connecting a new cable/flex to the ELV terminals on your boiler.
However, there are a lot of mains operated controls on an S Plan+ system, so I don't know how you intend to mix the voltages. Is this related to the posts about X Plan systems?

Thanks. Yes, I am trying to work out whether I have everything in place in case I want to do the D-Plan or X-Plan on an Intergas boiler. But I have always struggled with any sort of electrics!

I am using the diagram uploaded by @dilalio for D-Plan where the hot water timeswitch and cylinder stat are connected to 9 & 10 on the low voltage side of the PCB. Then I thought the rest of the S-Plan+ (both CH circuits) would connect to the switched live on the 230V side of the PCB.
 
Last edited:
Wouldn’t it just be the grey and orange from the motorised valves that send/receive the 24v to the boiler pcb?
 
Wouldn’t it just be the grey and orange from the motorised valves that send/receive the 24v to the boiler pcb?

My head's starting to spin! I get so confused by electrics. Can they send 24V. They currently have a 230V supply from the wiring centre.
 
I am trying to follow the diagram uploaded by @dilalio for D-Plan where the hot water timeswitch and cylinder stat are connected to 9 & 10 on the low voltage side of the PCB.
Yes, the LP811 could be used on the ELV pins 9 and 10.

The important point to note...
Screenshot_20241228_195518_Adobe Acrobat.jpg

The timer would be connected in parallel with the tank stat, and you would be using the normally closed terminals I.e. LP811 terminals 1 and 2.

The diagram you mentioned for anyone else's benefit...

Screenshot_20241228_200053_Adobe Acrobat.jpg
 
Yes they can. Grey and orange are kind of like volt free, you apply the voltage. The actuators need mains voltage to driven the motor. So live and neutral.

Have a look at this video

Thanks. That all makes a lot more sense now.

So, looking at the low voltage side, would I connect the oranges and greys from the two CH motorised valves to 6 & 7 where the roomstat is currently connected.

1735416713970.png
 
I need to say that I am not trying to do the full D-Plan or X-Plan at the moment with this design. I am just trying to work out how I might be able to trigger the boiler to give two different flow temperatures.
 
Last edited:
Thanks. What does in parallel mean? I thought they would go one after the other, but that sounds like in series.
One connected after the other, would be in-series.
The tank stat is connected, so that when it is satisfied, it will close the circuit, i.e. connecting together terminals 9 and 10 on X4.
Or put another way, with the tank up to temperature, terminals 9 and 10 are 'shorted' together.
Connecting (in parallel) the LP811 Normally closed terminals 1 and 2, to X4 terminals 9 and 10, will ensure a relatively safe way to provide this 'short circuit', when the hot water isn't required.
 
Thanks. That all makes a lot more sense now.

So, looking at the low voltage side, would I connect the oranges and greys from the two CH motorised valves to 6 & 7 where the roomstat is currently connected.

View attachment 367302
Apologies, I didn’t know about the X-plan or D-plan until I’ve just looked. They appear to use a different motorised valve, a diverter type by the look so of it, which only uses live and neutral, so I’m not sure where the 24v comes into play.
 
Apologies, I didn’t know about the X-plan or D-plan until I’ve just looked. They appear to use a different motorised valve, a diverter type by the look so of it, which only uses live and neutral, so I’m not sure where the 24v comes into play.

I think you actually were right.

As far as I can work out, the pins on the low voltage side trigger the boiler to start. Pins 6 and 7 trigger CH demand and pins 9 and 10 trigger DHW demand. And crucially, as far as I can tell, when you trigger the boiler on pins 9 and 10, the boiler changes to the higher DHW flow temperature and also causes pin 5 on the 230V side to become live. Pin 5 can then be used to energise a DHW zone valve.
 