I have just moved into a new house which has a Worcester Greenstar 4000 combi boiler .it is ran via a MYSON MEP2C controller with a wall mounted Drayton thermostat.I would like to change the controller over to a single channel hive receiver.
The thermostat will obviously need removing but i am unsure about how to go about changing the controller to the hive receiver
The controller is currently wired as follows
N L HW off CH off HW on CH on
Blue brown live / / brown brown

The HW on and CH on are live when required

The hive receiver only has
N L 1 2 3 4

I am unsure where the HW on and the CH on wires go on the hive reciever and what to do with the wiring for the redundant Dryton thermostat .
I have attached pics of the thermostat and the Myson controller wiring plates
IMG_4638[1].JPG

Any help would be most appreciated
 

Attachments

  • IMG_4646[1].JPG
    IMG_4646[1].JPG
    229.6 KB · Views: 114
The Hive has the same number of terminals. Are you sure it’s a combi, a bit odd to have both 3 and 4 in use for heating only. Although, 3 looks like it could be the live out to the room stat, but wouldn’t return on 4
 
Its def a combi boiler .terminal 3 (brown) says its HW on while terminal 4(brown) says its CH on.
I am fairly sure one of them comes from the room stat but not sure how to verify
 
The Greenstar 4000 Combi has a pre-heat facility [Assuming the version you have in Canada is the same as here in the UK] and the HW channel can be used to control the times when the pre-heat is operative.

Screenshot 2025-06-13 142759.jpg


Screenshot 2025-06-13 143306.jpg


So you can either swap the Myson MEP2C for a Two Channel Hive (which has exactly the same terminals as the Myson) and keep the pre-heat function, or install a Single Channel Hive and loose the pre-heat function.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top