choc block in socket
2 Feb 2013
Aberdeen
I'd like to use a choc block within a socket.
That means it'll be in an enclosure and be accessible. What about strain relief on that choc block though?
what strain would it be under?
try drilling 2 small holes in the back of the box and use a cable tie.
Curious why you want to use a choc bloc within a socket.
I assume they mean within the backbox of the outlet!
So why would this be done?
*If the cables are too short, it will help extend them. Is often required when changing socket plates, as the terminals could be in differing positions to the ones of the outlet that has been replaced or if you wish to move the socket positioning a few cms, if the existing cable lengths are not suitable or if someone has accidentally cut the conductors too short :oops: or they are broken/damaged.
*Also you can use them to alter the circuit configuration, if altering/extending the circuit. It is better done in a safe accessible space and the backbox meets that criteria.
Other reasons could be the safe termination of disconnected redundant cable or the termination of a cable that is to be connected at a later date.
Thanks PBoD. Just curious as the OP didn't say why and most posters usually do.
This invariably leads to a plethora of 'yes you can' or no you can't' responses. :lol:
I thought there wouldn't be much strain on the cables but just wanted to check as JB connections are with screws too but always need strain relief.
In this particular case, I'd like to extend the ring circuit.
In another case, I would like to move the socket further away but the cables are too short. I could make connections at the site of the current socket to extend the cables to the new socket site. However, I will be plastering then tiling over the area where the old socket will be. Will an MF connection box allow me to plaster over it, something of the Ashley type?
I would recommend if the joint was to be buried within plaster, to go down the route of crimping and heat shrink. I would hazard a guess that most MF connectors and enclosures, product data would not allow them to be rendered into walls, but would likely state can be used in underfloor situations. If you know the product you intend to use, it would be worth reading through the product data or even contacting the manufacture or linking on here so can browse and may be someone has an informed answer.
But you could if possible, pull the existing cables back and make the MF joints within a ceiling/floor void and extend back up to outlet with continuous cables, then no need to render in a joint.
Or just install new cables to extend and have no joints!
It's never that straightforward.
The cables drop from the ceiling once and run from socket to socket and includes the one I want to raise. The socket is behind a kitchen worktop which I will replace with one which will be higher, thus the need to raise the socket by about 15 cm.
What you propose is a lot of disruption and replastering for a mere 15 cm. If I could lay an extra 15 cm of cable, that will be 15 cm of digging into plaster and replastering. It won't even have to look pretty there because I will be tiling over it - but not up to the ceiling!