Choosing a radiator for a lobby

Joined
30 Jul 2006
Messages
3,481
Reaction score
338
Location
Hampshire
Country
United Kingdom
She who must be obeyed has taken a dislike to the radiator in our entrance lobby. The room is about 1.6M square with 2 outside walls and the front door, but no windows.
The present radiator is 750mm high by 500mm double with convectors, which I reckon would be about 1KW. It's well lagged by about 3 layers of coats hanging on pegs above it, but heats the lobby well.
We would like to fit a lower radiator , say, 400mm high, and anything up to the width of the room.

The various heat loss calculators I have tried indicate the heat loss to be about 500W, so it sounds like the present radiator is well OTT. Do you think 500W sounds about right for a small lobby with an outside door, or would you add a bit more to compensate for winter gales blowing through the letterbox :)
 
Sponsored Links
Worked it out according to your sizes and assume room height is 2.4M, no cavity insulation = 570 watts. I would fit a 600mm H x 500 W P+ or similar ;)
 
Thanks G4U. Your figure is just a tad higher than the highest from my calcs (the ceiling height is only 2.25M) so it looks like i'm in the right ballpark.

It looks like I will be shopping for a rad. around 300 X 1000 or 400 X 800, looking for about 600W / 2000BTU.
 