Hi all,

I have a 16amp breaker in my consumer unit and a 1.5mm 3 core SWA has been run 15 meters from this to a consumer unit outside. The consumer unit outside is a mini consumer unit and has 2 breakers in it, with a main switch.

1) What is the maximum amount of watts that can run on a 1.5mm 3 core swa

I wanted to run a 2-3kw external elector pond heater, but my calculations are telling me that this is not possibkle with this current setup, as it would be overloaded.

Please advise.

regards

andemz
 
Cable Size 1.5 mm
Voltage Drop 5.28 Volts.
Percentage Drop 2.3%
Current Load 13.0 Amps
Max Cable Load* 18.7 Amps

at 3kw of power

You have 16amp breaker that can supply 3.68kw of power.
 