combi boiler

Joined
13 Dec 2005
Messages
4
Reaction score
0
Location
Nottinghamshire
Country
United Kingdom
The pressure gauge on my boiler is reading above 3bar and water is coming out through expansion pipe outside. This is causing further problems inside my house as the outer wall is constantly wet. Any advise would be appreciated.[/b]
 
Check the advice in the sticky reference topic, especially re filling loop, as yours is probably not closed properly.
 
Only 2 reasons for overpressurising chrishutt stated 1 the other is dependant on model of boiler. If you have a twin pass heat exchanger this has failed if you have a secondary heat exchanger then that will need changing
 
which combi boiler is it.some are easy repaired some are not.
 