Conduit and Earthing Cables

R

rjuk

I'm wiring up a new garage in PVC conduit.

I'll be running three circuits down one piece of conduit and I was wondering if it was acceptable for them to share the same earth cable (rather than running 3x2.5mm2 - simply running a single piece) in an effort to comply with the cable capacity of the conduit?

I'm also going to be running some DC control cables in the garage - are the core colours for DC brown/blue or did they remain red/black?

Thanks in advance,
Ryan
 
Sponsored Links
no you can not use one earth wire for 3 ccts, and yes dc is red and black, you should not run dc with ac
 
hmm I was sure there was a reg that allowed it provided the earth wire was sized to meet the requirements for all the circuits.
 
Sponsored Links
Unearthed DC power circuit new colours Brown and Grey
Negative earthed DC power circuit Brown and Blue
 
From Table 51 (BS7671:2008)
For control circuits, ELV and other applications. Line conductors Brown, black, red, orange, yellow, voilet, grey, white, pink or turquoise.
For a neutral or mid wire blue (an earthed PELV conductor is blue)
 