Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
Because the OP is only running conduit for the drops so he can do the chases and make good beforehand. Through the floor/ceiling space it's not going to be in conduit I don't imagine.
If you do all the calculations including grouping, the CCC of 2 x 2.5mm² in conduit buried in plaster is slightly less than 20A and so doesn't really comply for a ring final. So you could only ever try to put 1 x 2.5mm² through, and this is pretty easy.
I will suggest that you run two 20mm or one 25mm conduit for ring circuits as getting 2x2.5mm² T&E into a 20mm tube from an awkward space is tricky. The same is true for more than 2x lighting cables.
If you do all the calculations including grouping, the CCC of 2 x 2.5mm² in conduit buried in plaster is slightly less than 20A and so doesn't really comply for a ring final. So you could only ever try to put 1 x 2.5mm² through, and this is pretty easy.
If you do all the calculations including grouping, the CCC of 2 x 2.5mm² in conduit buried in plaster is slightly less than 20A and so doesn't really comply for a ring final. So you could only ever try to put 1 x 2.5mm² through, and this is pretty easy.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local