Additionally, and I'm sure some of our resident gas fitters will correct me if I'm wrong, this is from BS 6891 (Quoted, Dingbat
)
'can be visually observed'............. visible??
So I suppose it depends on which set of regs trumps the other set of regs
8.16.4.2 Main equipotential bonding shall be connected:
a) on the customer's side of the meter;
b) as close as practicable to the meter before any branch in the installation pipework;
c) in a position where it is accessible, can be visually observed, and fitted with a warning label stating "Safety electrical connection. Do not remove.";
d) by a mechanically and electrically sound connection which is not subject to corrosion.
'can be visually observed'............. visible??
So I suppose it depends on which set of regs trumps the other set of regs