As you will have seen, it is said to have an 1800W 230V motor. The inrush current may trip a B16, but it certainly shouldn't need a "32A supply".What do the instructions say about the electrical supply requirements?
Kind Regards, John
As you will have seen, it is said to have an 1800W 230V motor. The inrush current may trip a B16, but it certainly shouldn't need a "32A supply".What do the instructions say about the electrical supply requirements?
Indeed, but it's probably a more likely (even if not all that likely!) bet than contemplating changing it to a B32 - the EFLI requirements (and ability to cope with inrush currents) would be the same in both cases (and quite possibly not satisfied) but, with the latter, it's also quite likely that the existing cable would not be adequate for a 32A OPD.It might be possible to change to a C-curve 16A breaker and alleviate the start-up trip problem, but that's still subject to existing wiring being suitable.
Yes, I saw that.As you will have seen, it is said to have an 1800W 230V motor.
Like you, I haven't seen any 'instructions' which say anything about that. However, I would assume that it requires the same supply as any other equipment which consisted (electrically) of just an 1800W motor - like a good few of the power tools I have, and at least one of my vacuum cleaners.Yes, I saw that. What do the instructions say about the electrical supply requirements?As you will have seen, it is said to have an 1800W 230V motor.
Indeed.Like you, I haven't seen any 'instructions' which say anything about that.
IMO if it's fitted with a plug, and the instructions do not specify any particular supply requirements, then if it does not work on any "valid" socket circuit it is not fit for purpose.HI, yeah standard 13a plug. don't believe it requires a 32 supply , have seen a few more comments where its the initial switching on that is tripping it. i'm happy enough the product is safe when connected to my internal sockets which are 32.
IMO if it's fitted with a plug, and the instructions do not specify any particular supply requirements, then if it does not work on any "valid" socket circuit it is not fit for purpose.HI, yeah standard 13a plug. don't believe it requires a 32 supply , have seen a few more comments where its the initial switching on that is tripping it. i'm happy enough the product is safe when connected to my internal sockets which are 32.
They're all 13A sockets, even if some are protected by a 32A MCB and others by a 16A one. The point is that, whilst a 16A MCB is more than adequate for the running current of the motor, its start-up current might trip a Type B 16A MCB. A 32A MCB would allow twice as much start-up current without tripping. ... so that could well be what you're experiencing. I have plenty of things with ~1800W motors which have never tripped anything, but I don't think I've never tried running any of them off a 16A circuit - they are always plugged in to 32A ring circuits.it does work on my two 32amp sockets inside house though, not sure why garage is 16amp but sure it was enough when installed.
Fair enough. I agree that there is almost certainly nothing wrong with the product, but I also agree with BAS that if it is known that there are likely to be problems if it is used on a 16A circuit, the instructions/specification really ought to say so.JohnW2, yeah thats pretty much where i am. don't think there is an issue with product, its in full working order in what i expected to be 32amp fuse. im happy to use extension in short term and will look to getting cables checked/upgraded if it becomes an issue.