Am thinking about having some power run to a large brick built stable in the autumn (no animals in it just tools) and am costing it out for now.
The run will be in 10mm 3 core swa and the lenth of run will be 75 mtrs. to new CU.
Total loading will be no more than 3kw. Cable size if calculated correctly should take into account the 4% VD. and cover the loop impedance okay.
The cable will be buried in part 1/2 mtr deep and clipped direct for the rest and will terminated in a 4 way rcd protected board and housed for extra safety in a box on the wall. Dont think earth spike will be needed as no water etc in stables. The largest load will be a 2kw shredder and taking diversity onboard logically would not be using it in dark so 1kw lighting will not be on. Think have done home work akay.
however at CU end can it terminate directly in RCD proctected side of split load.
Am thinking about having some power run to a large brick built stable in the autumn (no animals in it just tools) and am costing it out for now.
The run will be in 10mm 3 core swa and the lenth of run will be 75 mtrs. to new CU.
Total loading will be no more than 3kw. Cable size if calculated correctly should take into account the 4% VD. and cover the loop impedance okay.
The cable will be buried in part 1/2 mtr deep and clipped direct for the rest and will terminated in a 4 way rcd protected board and housed for extra safety in a box on the wall. Dont think earth spike will be needed as no water etc in stables. The largest load will be a 2kw shredder and taking diversity onboard logically would not be using it in dark so 1kw lighting will not be on. Think have done home work akay.
however at CU end can it terminate directly in RCD proctected side of split load.