Hi wondering if any of you kind gents could give me some advice.
I am about to buy a belling hob and double oven to fit myself . The manual for the hob states must be installed using a suitable double pole control unit,with 3mm minimum contact separation at all poles. It does not say what the min or max fuse protection should be . The only other info is the technical data which says -supply 220-240 50Hz 4.85kw- 6.20kw does this mean max load is 6.20kw ?
The oven says - The appliance must be installed
by a competent electrician using a
double pole control unit of
32 ampere minimum capacity,
with 3mm minimum contact
separation at all poles.
The technical info is - Electrical supply
220 - 240V ~ 50Hz
Load (Wattage)
4120W - 4900W
My consumer unit for the cooker is rated at 40a
What would you suggest for the best way to install these ?the hob + oven are less than 2m from cooker switch and it does not have a socket incorporated
Would it be possible to connect both these appliances together using the click 45a dual outlet plate for easier installation?
I am about to buy a belling hob and double oven to fit myself . The manual for the hob states must be installed using a suitable double pole control unit,with 3mm minimum contact separation at all poles. It does not say what the min or max fuse protection should be . The only other info is the technical data which says -supply 220-240 50Hz 4.85kw- 6.20kw does this mean max load is 6.20kw ?
The oven says - The appliance must be installed
by a competent electrician using a
double pole control unit of
32 ampere minimum capacity,
with 3mm minimum contact
separation at all poles.
The technical info is - Electrical supply
220 - 240V ~ 50Hz
Load (Wattage)
4120W - 4900W
My consumer unit for the cooker is rated at 40a
What would you suggest for the best way to install these ?the hob + oven are less than 2m from cooker switch and it does not have a socket incorporated
Would it be possible to connect both these appliances together using the click 45a dual outlet plate for easier installation?