As I said, applying diversity in relation to cable and protective device sizing (and total installation current requirement) is fair enough.If you think applying diversity to circuits and their equipment is inappropriate, then you have definitely missed something.
Well, for a start a 32A Type B MCB will (per generic spec - e.g. Fig 3.4 of the regs) will carry 50A for around 16 mins before tripping, and 46A/47A or so more-or-less indefinitely. That's why MCB sizing based on diversity calculations works, without lots of nusiance tripping.not really, from my understanding, the circuit is protected by a 32a mcb so will never pull 50amps anyway.
Thats a personal choice - I would apply diversity but also follow the manufacturers instructions. For example when fitting a double oven and hob together Hotpoint state they require a 45Amp dual pole cooker switch - thats good enough for me.Anyway, whatever the regs may require, I would personally be much more comfortable with a switch (or whatever) rated for the maximum current which could, under some circumstances, be drawn by the appliance, rather than the figure derived from applying diversity.
I suppose I'm pretty conservative in relation to such matters - and,as you say, it's a matter of personal choice. I cannot deny that even 'bare' compliance with regs (if that is achieved) is still compliance. However, a few questions:Thats a personal choice - I would apply diversity but also follow the manufacturers instructions. For example when fitting a double oven and hob together Hotpoint state they require a 45Amp dual pole cooker switch - thats good enough for me.
In analogy with what I've just asked riveralt about the 45A cooker switch, would the manufacturer's instructions for the 30A isolating switch you postulate indicate that it was OK to use it for a load which could be as high as 50A (and could certainly be considerably above 30A, indefinitely, without a 30/32A OPD operating)?30A plus 20A = 50A, which is 11.5 kW.
According to the On-Site Guide, "A 30 or 32 A circuit is usually appropriate for household or similar cookers of rating up to 15 kW.
That's good enough for me.
So is a 30 A isolating switch on a 30 A circuit.
However, a few questions:
- 1...I cannot find any reference in the regs to the application of diversity in determining the required rating of switches etc. Am I missing something, or are the regs simply silent on this issue?
This is an extract from the manual for the Hotpoint BD52P2 double oven. 'A double pole control switch having a minimum rating of 32 amps should be used to feed the cooker using a suitably rated cable. Where a hob is fitted adjacent to or over the cooker, a 45 amp Double Polce control switch should be used to feed both units via separate suitably rated cables'. So nothing about the load on the switch but then why would they - they are not making the switch.2...In the example you give, what do the manufacturer's instructions for the cooker switch say? Do they indicate that it's acceptable to use it to switch a load which could, at the time of operation, be more than 45A?
Nothing. See answer to 2 above.3...What, if anything, do the Hotpoint cooker instructions say about the maximum possible current draw and protective device requirements?
However, a few questions:
- 1...I cannot find any reference in the regs to the application of diversity in determining the required rating of switches etc. Am I missing something, or are the regs simply silent on this issue?
- The OSG adds to reg 311 but makes no reference to switches - nor to cooker connection units.
So am I, but proper design practice should not rely on built-in 'safety margins' over and above an accessory's rating. I'm less sure about the 30A switch suggested by Stoday, even though that is still within the load calculated using diversity - has anyone tried breaking a 50A current with a 30A-rated switch? Still possibly OK, but I imagine that it goes way beyond normal 'built-in safety margin' of the rating.[quoteI'm also sure that, just like the MCB, a 45Amp cooker switch will not burst into flames at 46Amps.
That's no use - Hotpoint don't make the switch! I was asking what the instructions provided by the manudacturer of a 45A switch would say about it's suitability for switching a load potentially as high as 50A.This is an extract from the manual for the Hotpoint BD52P2 double oven.....2...In the example you give, what do the manufacturer's instructions for the cooker switch say? Do they indicate that it's acceptable to use it to switch a load which could, at the time of operation, be more than 45A?
They don't say what maximum current their appliance draws?Nothing. See answer to 2 above.3...What, if anything, do the Hotpoint cooker instructions say about the maximum possible current draw and protective device requirements?
I don't really think Hotpoint's guarantee comes into this. Their guarantee only covers their appliance, and I really can't see how the rating of a switch in the circuit supplying it could possibly affect the appliance!As far as Hotpoint are concerned if I follow their instructions then they will honour their guarantee - they are happy to utilise a 45 Amp cooker switch to control both oven and hob - therefore so am I.
What a load of codswallop - The whole of BS7671 is about built in saftey margins and as a practitioner I will continue to follow its guidelines for diversity.So am I, but proper design practice should not rely on built-in 'safety margins' over and above an accessory's rating.I'm also sure that, just like the MCB, a 45Amp cooker switch will not burst into flames at 46Amps.
That's your prerogative. BS7671 itself doesn't actually give any guidelines (but the OSG gives some); 311.1 merely states that diversity may be taken into account in assessing maximum demand and as we've discussed, there is certainly no guidance (in either BS7671 or OSG) in relation to the ratings of items such as switches.What a load of codswallop - The whole of BS7671 is about built in saftey margins and as a practitioner I will continue to follow its guidelines for diversity.So am I, but proper design practice should not rely on built-in 'safety margins' over and above an accessory's rating.I'm also sure that, just like the MCB, a 45Amp cooker switch will not burst into flames at 46Amps.
Is diversity to be used for designing individual circuits?
Or is its purpose to provide an assumed load to be used in assessing the maximum demand of the whole installation?
Is diversity to be used for designing individual circuits?
Or is its purpose to provide an assumed load to be used in assessing the maximum demand of the whole installation?