Did you notice it was the rcd from the other post.
I had to take the earlier pictures for the insurance claim for the over voltage.
That was before it happened.
spark 123
The rcd was only 100amp 100ma fed with 25 mm tails from connecter boxes also teeing off with 25mm to a second same type board,the connector boxes fed with what looked like 35mm from a 200a head with 160a "J" fuses in.
This did not seem good to start with.
The board had to come and replace the fuses after, to get the rest of the site back on.(after the fire brigade left)
I remember once pressing the reset on a power breaker socket and that exploded, so I think I may be jinxed with RCD's.
I too wondered if it was internally damaged or on its last legs, possibly accelerated due to the original problem, over the years it had also been run and possibly overloaded, with a full load of industrial catering equipment.
This was all now redundant since the 90's according to the staff, so I presume the rcd had never been touched for over ten years.
Till I disturbed it maybe.
Must say it was the scariest and most embarrising day of my career.
The flash burnt my hand , but thankfully that was it.
The cut out was the other side of the fire, and was one with the four knurled nuts , two wire seals, and inside was the porcelein holders with the two wing nuts to remove them.
There was no safe way to get in and pull them, the room was about 8foot by 3foot,
So I stayed outside behind the firedoor and fired the co2 onto it, it went out for seconds then just arced and reignited.
Them 160 a hrc's took a lot to blow.