Yes 1.5mm is suitable cable for a 10A MCB
Electrically speaking, yes - but you need to be sure that there is enough space for all the cables and, more importantly, that you can comfortably and satisfactorily get three conductors into each of the terminals in the connector.Having opened the first light to take a feed from it, I’ve discovered that it is already feeding the existing second light. See pic. Can I still take a feed for a third light?
You can take the feed for the fourth from either the second or the (new) third, whichever is more convenient.And can I then take feed from the existing second light to the fourth?
Thank you John. Yes you’re right, there’s not enough room in the lamp’s terminals for there cables. I’ll have to add a choc bloc in the lamp for the three cables then add a short length of cable to lamps terminals.Electrically speaking, yes - but you need to be sure that there is enough space for all the cables and, more importantly, that you can comfortably and satisfactorily get three conductors into each of the terminals in the connector.
Kind Regards, John
Well, I can't tell without looking, but a 'nicer' solution (avoiding an additional choc block), if it were possible, would be to replace the unit's existing 'terminal block' (which itself may well just be some type of choc block) with one large enough to take all the conductors.Thank you John. Yes you’re right, there’s not enough room in the lamp’s terminals for there cables. I’ll have to add a choc bloc in the lamp for the three cables then add a short length of cable to lamps terminals. Not ideal but I can’t thinkbof anything else?
Hi John, the trouble with that is that I then end up with a maze of conduit on the ceiling.Well, I can't tell without looking, but a 'nicer' solution (avoiding an additional choc block), if it were possible, would be to replace the unit's existing 'terminal block' (which itself may well just be some type of choc block) with one large enough to take all the conductors.
However, would it not be convenient to take your third light from the second, and the fourth from the third (which should avoid 'terminal capacity' issues)?
Kind Regards, John
Why do you need conduit?Hi John, the trouble with that is that I then end up with a maze of conduit on the ceiling.
That looks fine. Nothing will get overloaded.This is what I’ve done - see pic. The two white cables are the free in and the feed for the second lamp. I’ve added the two grey cables - one for the new third light. Then the other grey goes to the terminals in the lamp. I’m not at risk of overloading something by having just one cable carrying all the load to the terminals am I?
I’m using that white plastic conduit to put the cable into. I thought it was a good idea to use it but also it’s what the original builder used for the first two lights.Why do you need conduit?
Some purist may comment on the very small bit of bare copper visible for one of the conductors in the top-right terminal of the chock block
Kind Regards, John
You're welcome.Anyhow, all done now and it all works perfectly! Many thanks for your help!
Hello again, thinking of the cable to buy - would 1.5mm twin core plus earth be right?
Many thanks